Electrical Issue Question

I am hoping someone can give me a general idea of what may be causing the problem I am having.

For a couple of weeks I have noticed that when I run anything additional to my regularly plugged in electrical items, I get a "browning down" on my lights. I notice it particularly when I run my hair dryer, flat iron, vacuum and washer and drier. If I am in the kitchen with the refrigerator running and I start the microwave, not only do the lights brown down, but I can hear the pull on the refrigerator motor as well.

I have been in this house (built early 1970s) for ten years now and have never experienced this problem before. I am not running anything new or different than I ever have. Any idea what the problem might be?

Thanks in advance for any responses.

FTM
Foxterriermom is offline   Reply With Quote
Old 10-17-2014, 12:01   #2
peng
Senior Member
 
peng's Avatar
 
Join Date: Nov 2011
Posts: 232
Something is making your system think its overloaded.

Check your fuse breakers - may need to replace or get a different type.

Barring that simple explanation - call an electrician. I'm an engineer and dealing with electricity gives me the willies.
peng is offline   Reply With Quote
Old 10-17-2014, 12:30   #3
9jeeps
Fogey
 
Join Date: May 2004
Location: at the end of the road
Posts: 4,397
I also had the same problem with my system last spring. It had been flustrating me for a couple years and burning up Breakers. One day I occurred to me to check my incoming lines.(I have underground service) One leg was 110V the other leg was off and on at 50-80 volts... It should have also been 110V.

I called PUD at 3;30 on Friday after noon. They hustled right out and began to dig holes in my easement. found like three bad spots in the lncoming line and had to repair them. All has been well since.
__________________
FOGEY
Trying to make
sense of it all.
9jeeps is offline   Reply With Quote
Old 10-17-2014, 12:35   #4
Resqu2
Senior Member
 
Resqu2's Avatar
 
Join Date: Aug 2007
Location: SouthWest VA
Posts: 4,865
4 of the 5 things you listed are a big pull but if you never had a problem before I don't know why you would now? Almost like the power co isn't giving you enough power? If you were over doing a circuit the breaker would just kick.
__________________
A gun in the hand is better than a cop on the phone.
Resqu2 is online now   Reply With Quote
Old 10-17-2014, 12:39   #5
Cubdriver
Senior Member
 
Cubdriver's Avatar
 
Join Date: Aug 2005
Location: Southeastern Litchfield County, CT
Posts: 2,138
Get someone in to check the connections and voltage at the panel. Line to line and line to neutral with various things operating. It's possible that there's a slightly bad connection that's doing weird things when current is drawn.

There was a high resistance connection in the neutral between the pole and house at my ex's a few years ago; it was causing one side of the line to drop and the other to go high when things like the microwave were on and drawing power. Lights on the same 'side' of the panel as the microwave would dim, and those on the other side would brighten as their supply voltage increased. It took a while to figure out, but was an easy fix (new compression connector) once it was diagnosed.

All that probably makes no sense to you, but in short, get someone to check voltages at the panel and make sure nothing's loose.

Good luck with it.

-Pat
__________________
Speed has never killed anyone. Suddenly becoming stationary… that's what gets you.. (J. Clarkson)
Cubdriver is online now   Reply With Quote
Old 10-17-2014, 12:44   #6
DWARREN123
Grumpy Old Guy
 
DWARREN123's Avatar
 
Join Date: Jan 2008
Location: CLARKSVILLE TN
Posts: 4,545
Also check to see if you may possibly have aluminum wiring. Bad stuff.
Sounds like either bad incoming voltage or connection.
__________________
Have a Nice Day
DWARREN123 is offline   Reply With Quote
Old 10-17-2014, 12:59   #7
Cubdriver
Senior Member
 
Cubdriver's Avatar
 
Join Date: Aug 2005
Location: Southeastern Litchfield County, CT
Posts: 2,138
Quote:
Originally Posted by DWARREN123 View Post
Also check to see if you may possibly have aluminum wiring. Bad stuff.
Sounds like either bad incoming voltage or connection.
Excellent point - the house was built in the right time frame to potentially have it. It's ok for the service entrance, but not good if it's used for the distribution within the house...

http://wikipedia.org/wiki/Aluminum_wire

-Pat
__________________
Speed has never killed anyone. Suddenly becoming stationary… that's what gets you.. (J. Clarkson)
Cubdriver is online now   Reply With Quote
Old 10-17-2014, 13:04   #8
pipedreams
Member
 
pipedreams's Avatar
 
Join Date: Feb 2011
Location: S. E. Iowa
Posts: 4,080
Since you said you are doing nothing different I would call the utility company. I had a similar problem and when they came out they replaced the pole transformer and the lines to the meter. No problems since then.
__________________
NRA Patron Member
GOA Life Member


Never look down on anybody, unless you're helping them up.
pipedreams is online now   Reply With Quote
Old 10-17-2014, 13:09   #9
Foxterriermom
Senior Member
 
Foxterriermom's Avatar
 
Join Date: Mar 2009
Location: Lone Star State
Posts: 3,246
Gentlemen, thank you so much for your responses. I appreciate the time you took to give me your feedback.
Foxterriermom is offline   Reply With Quote
Old 10-17-2014, 13:20   #10
G29Reload
Tread Lightly
 
G29Reload's Avatar
 
Join Date: Sep 2009
Posts: 12,509
Quote:
Originally Posted by DWARREN123 View Post
Also check to see if you may possibly have aluminum wiring. Bad stuff.
Sounds like either bad incoming voltage or connection.
Can be but not necessarilly a disaster.

AL expands and contracts a lot more than copper so it can loosen connections. At the low end, light switchgear like switch and plug is done by a house mouse or other apprentice. AL is retained today for SEU (service entrance unarmored) because its installed by journeymen or higher who can put a torque wrench on connections and also use antioxidants like NoAlux which is made by Ideal. Theyre also overseen by the master license holder.

Alum romex should be replaced where you can, but checking connections periodically can hold you over if you can keep them tight till you rewire. Check each outlet w the power off and tighten with a screwdriver.

All the appliances listed are 12+ amps and most light strings are 15amp limit on 14 ga copper wire and a matching 15a single pole breaker with a maximum of 10 devices or outlets per run. You push it to the max the lights are going to dim.

A fridge should be on its own dedicated line. Same for a mw.

Toasters and blenders also pull some amps so it does not hurt to have a couple of kitchen counter outlets on 12ga wire with 20a breakers.

You should also have a balanced panel and not have all the breakers running down one side or you can pull feedback on the neutral.

If your house is squared away and still problems, call the power company.
__________________
Avenge me...AVENGE ME!

To view links or images in signatures your post count must be 10 or greater. You currently have 0 signatures.
G29Reload is online now   Reply With Quote
Old 10-17-2014, 13:29   #11
Foxterriermom
Senior Member
 
Foxterriermom's Avatar
 
Join Date: Mar 2009
Location: Lone Star State
Posts: 3,246
Quote:
Originally Posted by DWARREN123 View Post
Also check to see if you may possibly have aluminum wiring. Bad stuff.
Sounds like either bad incoming voltage or connection.
You know, I just changed a malfunctioning wall plug the other day and did see at least one copper wire when I fixed that. Couldn't tell you if the other line was copper of not.

I did just call the power company and they are going to check my service for me.
Foxterriermom is offline   Reply With Quote
Old 10-17-2014, 13:33   #12
gwalchmai
Lucky Member
 
gwalchmai's Avatar
 
Join Date: Jan 2002
Location: Outside the perimeter
Posts: 46,278


Early onset Glaubner's Disease, or I'll eat a bug. The only thing that would confirm it further is if sometimes you sneeze when suddenly exposed to bright sunlight, or occasionally find yourself strangely attracted to vanilla ice cream.
gwalchmai is offline   Reply With Quote
Old 10-17-2014, 13:34   #13
BobbyS
You Talkin ToMe
 
BobbyS's Avatar
 
Join Date: Feb 2010
Location: In The Noise
Posts: 3,016
Quote:
Originally Posted by 9jeeps View Post
I also had the same problem with my system last spring. It had been flustrating me for a couple years and burning up Breakers. One day I occurred to me to check my incoming lines.(I have underground service) One leg was 110V the other leg was off and on at 50-80 volts... It should have also been 110V.

I called PUD at 3;30 on Friday after noon. They hustled right out and began to dig holes in my easement. found like three bad spots in the lncoming line and had to repair them. All has been well since.
On my house I want to see 120 volts on each line.
__________________
I don't mind shooting, as long as the right person gets shot! - D. Harry
BobbyS is offline   Reply With Quote
Old 10-17-2014, 13:57   #14
9jeeps
Fogey
 
Join Date: May 2004
Location: at the end of the road
Posts: 4,397
You're right ! That's what I was getting only on one side. The other side was variable.
I will delete my former post.

In my service repair they found nicks in the under ground wire and had to cut out the bad that was leaking to earth. There were three eruptions in the lines and said there could be more in the future.

My service is over 35 years old and they ask me if it happens again if I would be open to an above ground service to the meter with a pole in my yard some where from the transformer.
We agreed that would be the way to go. Also my entrance cable to the meter is aluminum.
__________________
FOGEY
Trying to make
sense of it all.
9jeeps is offline   Reply With Quote
Old 10-17-2014, 15:00   #15
Cubdriver
Senior Member
 
Cubdriver's Avatar
 
Join Date: Aug 2005
Location: Southeastern Litchfield County, CT
Posts: 2,138
Quote:
Originally Posted by G29Reload View Post
You should also have a balanced panel and not have all the breakers running down one side or you can pull feedback on the neutral.
Agreed on a balanced load, but I have one nit to pick here. In every panel I've seen, it's ok to have breakers running down one side only - the connections on the bus alternate L1-L2 repeat (or L1-L2-L3 repeat for three phase before some pedant points it out ) and continue in this pattern down to the bottom, otherwise a 2 pole breaker would not be able to supply 240 V. from two adjacent taps.

-Pat
__________________
Speed has never killed anyone. Suddenly becoming stationary… that's what gets you.. (J. Clarkson)
Cubdriver is online now   Reply With Quote
Old 10-17-2014, 22:25   #16
Paul53
Geezer Boomer
 
Paul53's Avatar
 
Join Date: Nov 2011
Location: Corner of walk & Don't Walk
Posts: 4,235
Quote:
Originally Posted by gwalchmai View Post
Early onset Glaubner's Disease, or I'll eat a bug. The only thing that would confirm it further is if sometimes you sneeze when suddenly exposed to bright sunlight, or occasionally find yourself strangely attracted to vanilla ice cream.
There's no cure for Glaubners disease except death. You should have told him that.
Also, measure your circuits, make sure you don't have a short one.
__________________
Every living human has DNA that traces back to Africa. All the wars are about differences we've invented or chosen.
Paul53 is offline   Reply With Quote
Old 10-17-2014, 22:51   #17
racer11
Senior Member
 
Join Date: Jul 2005
Location: Eastern Kansas
Posts: 2,451
The low voltage could harm any electrical motor you have running such as your fridge,,,first have the inbound lines checked for low voltage,,,I had the same issue with my cabin and discovered that the line leading to the building was rubbing on a tree limb. The insulation rubbed off and caused a large voltage drop and that caused the motor in my fridge to burn up. My lights would do the same as you described.
__________________
Growing older is not a choice but acting older is optional
racer11 is offline   Reply With Quote
Old 10-17-2014, 23:02   #18
Foxterriermom
Senior Member
 
Foxterriermom's Avatar
 
Join Date: Mar 2009
Location: Lone Star State
Posts: 3,246
Quote:
Originally Posted by racer11 View Post
The low voltage could harm any electrical motor you have running such as your fridge,,,first have the inbound lines checked for low voltage,,,I had the same issue with my cabin and discovered that the line leading to the building was rubbing on a tree limb. The insulation rubbed off and caused a large voltage drop and that caused the motor in my fridge to burn up. My lights would do the same as you described.

Thanks! Two weeks ago I was up on the roof cutting back the neighbor's tree that had grown into my lines that came off the pole and fed into the house. I didn't look closely at the lines as at the time I was just trying not to cut the wrong thing and electrocute myself. I'll go back up sometime this weekend and see if there is any visible wear.
Foxterriermom is offline   Reply With Quote
Old 10-18-2014, 01:11   #19
BobbyS
You Talkin ToMe
 
BobbyS's Avatar
 
Join Date: Feb 2010
Location: In The Noise
Posts: 3,016
Quote:
Originally Posted by Foxterriermom View Post
Thanks! Two weeks ago I was up on the roof cutting back the neighbor's tree that had grown into my lines that came off the pole and fed into the house. I didn't look closely at the lines as at the time I was just trying not to cut the wrong thing and electrocute myself. I'll go back up sometime this weekend and see if there is any visible wear.
Let the power company check it. That part of the feed is their responsibilities in most areas. If insulation is rubbed off you could get zapped!
__________________
I don't mind shooting, as long as the right person gets shot! - D. Harry
BobbyS is offline   Reply With Quote
Old 10-18-2014, 01:30   #20
silentpoet
Senior Member
 
silentpoet's Avatar
 
Join Date: Jan 2007
Location: This Old Caddy
Posts: 17,261
Quote:
Originally Posted by BobbyS View Post
Let the power company check it. That part of the feed is their responsibilities in most areas. If insulation is rubbed off you could get zapped!
On the positive side it won't happen to you twice.
silentpoet is offline   Reply With Quote

 
  
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump




All times are GMT -6. The time now is 12:56.




Homepage
FAQ
Forums
Calendar
Advertise
Gallery
GT Wiki
GT Blogs
Social Groups
Classifieds


Users Currently Online: 1,084
281 Members
803 Guests

Most users ever online: 2,672
Aug 11, 2014 at 2:31