If I was running 110 volt (or 115 or 120) AC 300 or so feet I would want to use at least #12 2+g underground cable, and use conduit to bring it above ground. #12 is nominally good for 20 amps, but I would not expect to run more than about 15 amps load due to voltage drop at that distance.


Posted using Outdoor Hub Campfire
Rule of thumb is to go up one wire size for every 100'

15A circuit normally would use #14, for 300' run use #10